[英]pymodbus read meter registers
我是Modbus的新手,但是我有一個小項目需要處理。 我需要從電表讀取一些值。 我是從互聯網上的一些示例中編寫的:
import logging
from pymodbus.client.sync import ModbusTcpClient as ModbusClient
logging.basicConfig()
log = logging.getLogger()
log.setLevel(logging.DEBUG)
client = ModbusClient('192.168.80.210')
client.connect()
rr = client.read_holding_registers(40012, 1)
print rr
client.close()
似乎正在連接到儀表,因為這是我的輸出:
DEBUG:pymodbus.transaction:Current transaction state - IDLE
DEBUG:pymodbus.transaction:Running transaction 1
DEBUG:pymodbus.transaction:SEND: 0x0 0x1 0x0 0x0 0x0 0x6 0x0 0x3 0x9c 0x4c 0x0 0x1
DEBUG:pymodbus.client.sync:New Transaction state 'SENDING'
DEBUG:pymodbus.transaction:Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
DEBUG:pymodbus.transaction:Transaction failed. (Modbus Error: [Invalid Message] Incomplete message received, expected at least 8 bytes (0 received))
DEBUG:pymodbus.framer.socket_framer:Processing:
DEBUG:pymodbus.transaction:Getting transaction 1
DEBUG:pymodbus.transaction:Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
Modbus Error: [Input/Output] Modbus Error: [Invalid Message] Incomplete message received, expected at least 8 bytes (0 received)
我想從寄存器40012
讀取到40014
,這是我擁有的Modbusdbus映射: Modbus映射
我感謝您的幫助。 問候,
我認為您應該設置unit
和port
參數,並使用rr.registers
來獲取該值,因此您需要知道unit_ID值以及設備端口。
在大多數情況下, unit
是1
, port
是502
作為modbus的默認值。
如果要從地址40012
到40014
進行讀取,則可以從40012
讀取,其count=3
。
我改進了您的代碼,嘗試一下:
from pymodbus.client.sync import ModbusTcpClient
client = ModbusTcpClient('192.168.80.210', port=502)
if client.connect():
res = client.read_holding_registers(40012, count=3, unit=1)
if not res.isError():
'''.isError() was implemented in pymodbus version 1.4.0 and above.'''
print(res.registers)
else:
# handling error
print(res)
client.close()