Error fetching data from Rockwell OPC UA Server using Eclipse Milo JAva Client

I have built a Java Application to fetch data from OPC UA Server. I have used Eclipse Milo UA Client SDK to build the client. I am facing a problem in OpcUaClient.readValues method. I am passing a list of NodeId created from Tags defined and if I traverse the DataValue array returned by readValues method, I get follwing error for some of the elements

DataValue{value=Variant{value=null}, status=StatusCode{name=Bad_NodeIdUnknown, value=0x80340000, quality=bad},

Sudo code looks like

List<NodeId> nodeIds = new ArrayList<NodeId>();
List<Parameter> parameters = device.getParameters();
for (int i = 0; i < parameters.size(); i++) {
    Parameter parameter = parameters.get(i);
                            
    nodeIds.add(new NodeId(device.getNsID(),  parameter.getTagName()));
                            
}
List<DataValue> values = client.readValues( 0.0, TimestampsToReturn.Both, nodeIds).get();
for (int i = 0; i < values .size(); i++) {
    DataValue dvalue = values.get(i);
    if( dvalue.getValue().getValue() != null) {
        Integer intValue =  (Integer) values.get(i).getValue().getValue();
                            
        logger.info("captured Value is  {}", value);
                                        
    }
    else
    {
       logger.error("Error fetching value for {} , {}", parameter.getName(),dvalue.toString());
    }
}

The error is flagged from else clause.

My application is running on a separate computer than the SCADA Server ( OPC UA). A peculiar behavior observed is, If I use ProSys Client to check value of failing tag, and if I re-run my application, data is fetched correctly. I am completely clueless about how ProSys client and my application is related. Is prosys client triggering something on the server side to load the tags in some cache... Any clues/pointers will help. Thanks in advance.

It sure sounds like the Rockwell server doesn't actually "build" the Node instances until you've browsed it first.

You aren't doing anything wrong in the client; this is stupid behavior on the server's part. You may have to program your client to recursively browse the hierarchy you're interested in before reading or creating monitored items.